Two MPPT 250/60 in parallel. Do I have to adjust the individual current?

Hi Community,

nowadays I am running one MPPT 250/60 with one MP II 3000 and two Pylontch 2000c batteries. The MPPT current setting is at 50 Amps.

Question: When I add another MPPT 250/60, do I have to set the max load current to 25 A on per MPPT? In order not to over charge the battery pack with more than 50 Amps?


Thanks for your advice.


Kurt







Multiplus-IIMPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nickdb avatar image
nickdb answered ·

If the pylons are setup correctly with dvcc they will control the chargers, no need to manually limit them.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alex Leo avatar image
Alex Leo answered ·

If you set the current at 25A the MPPT will put out only 25.So what is the point of limiting its power ?Instead of having 1 MPPT pushing 60 amps you want to put another one and limit both at 25 ? Also if US2000C BMS works in the same way as the US3000C,when it detects higher currents than what the battery can take it will turn off your MPPT.