question

romarub avatar image
romarub asked

Temperature compensation of charge voltage

Hello colleagues,

We need to make a 24 volt system without an inverter (there are no AC consumers on site), with gel batteries, BMV-702 and Cerbo GX. We want to measure the midpoint voltage and battery temperature to compensate for the charge voltage. As far as I understand, the BMV-702 allows you to do only one of these. My question: if we connect the temperature sensor ASS000001000 (for Quattro, MulitPlus & GX Device) to Cerbo, and in the settings we select the “battery” role for it, will the data from it be able to influence the charge voltage from the MPPT? Or will it just be a passive temperature measurement?

MPPT ControllersTemperature Sensor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
theo74 avatar image
theo74 answered ·

To extract the equipment from your question:

1. BMV-702

2. Cerbo GX

3. Victron temp sensor

4. MPPT (Victron?)

Indeed you can messure the midpoint voltage of the batteries with the external input of the BMV-702 shunt. In this case you can set an alarm when the midpoint voltage deviates too much. But in this case you've used the external input of the shunt for the midpoint voltage, and therefore can not be used for a temperature sensor anymore.


When you connect the Victron temperature sensor on to the Cerbo GX, indeed you can create a role in the Cerbo GX menu/software. In this case you could assign one of the Cerbo's relais connections, and make a minum and maximum temperature in between which the relais should be closed or open. The Cerbo GX relais connections are limited to 4A maximum of current, so a bigger relais connected on to the Cerbo relais could be mandatory, to switch on/off bigger load/charge currents.


When you have a Victron Smart MPPT, you could also take a cheap Victron Smart Battery Sense module which is capable of both monitoring the battery voltage, as well as the battery temperature. If you setup a Bluetooth Victron "Ve Smart Networking" network, and connect the Victron MPPT with the Smart Battery Sense in this network, they can work together, and you can set the MPPT so that it will shut off at a to high/low battery temperature.

When using more than one battery, more than one Victron temperature sensor, or Smart Battery Sense could/must be used.


I'm not to experienced with the Cerbo GX, but maybe it's also possible to control a Victron Smart MPPT via an external temperature sensor on the Cerbo GX, directly in a Ve Smart Network, without using one of the Cerbo GX relais connections. Maybe other forum members will know a solution in this option.


2 |3000