Victron 200ah smart battery cable run size

Do cable runs between each of four Victron 200ah smart batteries and a Lynx Distributor #1 (on left side of Lynx BMS) require 4/0 cable? Or would 2/0 be sufficient? I will be using 4/0 cable between the 3000 Multiplus II inverter/charger and the Lynx Distributor #2 on the right side of the Lynx BMS.

Lithium Battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

Size for current. As we have no idea of loads, we can't answer the question.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bradleyasmith avatar image bradleyasmith commented ·

Max current draw of 225 amps, for short period. Usually much less.

Refrigerator 1.5 amp

Fan 2 amp

Lights 1.5 amp

Water pump 7.5 amp

12V AC 58 amp

Cooktop 140 amp

Microwave 80 amp

0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ bradleyasmith commented ·

You can split the total load by 4 between the batteries.

Best cable for theoretical max.

Maybe AWG 3 or 2 to the lynx.


0 Likes 0 ·
bradleyasmith avatar image bradleyasmith kevgermany ♦♦ commented ·
Thanks!
0 Likes 0 ·