Adding a 230v Multiplus to a Quattro 120v marine system

We want to add 230VAC 50Hz to our existing 120VAC 60hz boat. The 120 Quattro and 230 multi both have neutral to chassis therefore to ground, I anticipate issues having the two voltages and frequencies tied to the same ground? I know boat are using this system anyone have input on this issue?

TIA

Seamus

[moderator note: edited voltages for accuracy and clarity]

MultiPlus Quattro Inverter Charger
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mike Dorsett avatar image Mike Dorsett commented ·
The biggest issue here is any leakage from the live (active) lines. Bear in mind that due to the different frequencies, the 230V system, which has a peak instantaneous voltage of 352V, and the 120V system with peak instantaneous voltage of ~170V will be out of phase every 0.1 seconds. This gives a peak instantaneous voltage of 495V. as well as using RCCD's on both systems, all AC wiring will need to be carefully segregated.