kp4djt asked

DC Load always shows zero

Folks, I am using a SmartShunt as a load meter. I can see it in the devices, it shows the load going through it but it does not show any load in the graphic.

1697672772948.png


If I look at the devices they are certainly there here is the Remote Console view

1697672854847.png

Another view of Device list
1697672948032.png

And the expanded view for DC Load which is the SmartShunt
1697673007648.png


All appears to be working but I cannot get the SmartShunt to show the flow of power to the load.


I have set it up as a meter rather than a battery device.


Energy Meterdc meter
1697672772948.png (57.4 KiB)
1697672854847.png (42.8 KiB)
1697672948032.png (20.1 KiB)
1697673007648.png (41.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Kevin Windrem avatar image
Kevin Windrem answered ·

I think you need to program the shunt for DC System, not DC Load. Yes, that's a bit confusing. DC System has always calculated "other" DC loads and sources and the DC meter setting for DC System is intended to mimic that.

I suppose DC loads could be separated from DC charging sources and if only DC loads are present, the tile could be renamed, but that's for later and a low priority at that.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kp4djt avatar image
kp4djt answered ·

Thank you very much that took care of it, went right in and changed to DC system and it showed right up.