MPPT 450/100 False BMS error 67

Getting false reports and causing complete shut down on inverter side of system it will repeat this error in a loop about every 15-30 mins.

Victron 48v/5000 inverter

18 270w panels

victron 450/100 MPPT

Lithionics 51v 630ah battery bank

Lithionics is tied to the Cerbo via VE CAN. VE Can network setup as RV-C

This issue has happened ever since doing the 1.11 firmware on the 450/100. Is there any way to revert the firmware back to 1.10 or 1.08. I looked on the victron page to find the older firmwares but do not see any previous firmwares listed for the solar controllers.

MPPT ControllersBMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@wiringOCD

See attached.

Although if the whole system is shutting down I would wonder how often the BMS is sending a signal? The GX will give that error usually after quite a few minutes of no contact.


MPPT_RS_450-100A_A110_v01.10_044858.zip