Hello,
I have a problem with a Venus GX device. The Remote Console and VRM features are painfully slow on this device. I have checked D-bus round trip, and it is increadibly high, it never goes below 300ms, and reaches 3000-4000ms every day when the MPPTs are working. I have checked the cabling, every communication line seems to be fine, lugs are crimped well and screws are torqued down correctly. What could cause such an issue? Did anybody experience similar problem, how can I resolve this?
In the system we have 2 VE.can MPPTs, 2 Multiplus II in parallel and 1 VE.direct BMV, so I don't think that the system is too complex for a Venus GX. Modbus TCP, MQTT services are disabled, normal OS is installed not large OS.
I checked Dbus round trip time for a long period, and it was quite normal before 22nd of July 2023, but after that it is constantly high. There was no firmware update at that time, and now after I updated the Venus OS from v2.94 to v3.11 the issue doesn't changed.
I have checked VRM diagnostics, and all values seemed to be okay, except the "Boot type" reporting "watchdog-EMAXLOAD (load average too high)", see table down below.
I could use any help in this topic as I never saw something similar. Nevertheless, the system still runs fine, but working with it (changing setup, check data and operation) is painful and VRM operations usually ends with an error because of no response or timeout from the Venus.
Date/ time | Data attribute code | ||||
---|---|---|---|---|---|
24 minutes ago | Gateway | 0 | d (1) | gatewayID | Venus OS |
24 minutes ago | Gateway | 0 | mi (386) | Productid | C002 |
24 minutes ago | Gateway | 0 | mn (387) | MachineName | Venus GX |
24 minutes ago | Gateway | 0 | v (2) | Fw Version | v3.11 |
24 minutes ago | Gateway | 0 | build (3) | Fw Build date | 20231009045315 |
24 minutes ago | Gateway | 0 | ms (556) | Machine serial number | (removed for privacy) |
24 minutes ago | Gateway | 0 | cp (453) | Capabilities | MQTT-RPC; MQTT-RPC new firmware update command; VNC-SSH authentication; VregLink; Multiple generator start-stop services is supported; Accumulated generator runtime is available on the Tga attribute.; Has Dynamic ESS support (1111111) |
24 minutes ago | Gateway | 0 | dg (985) | Default gateway | Wifi |
24 minutes ago | Gateway | 0 | w (237) | Boot type | watchdog-EMAXLOAD (load average too high) |
24 minutes ago | Gateway | 0 | rss (154) | Remote support | Enabled |
24 minutes ago | Gateway | 0 | rsIpPort (543) | Remote support IP and port | (removed for privacy) |
7 minutes ago | Gateway | 0 | ipr (148) | Remote ip address | (removed for privacy) |
24 minutes ago | Gateway | 0 | ip (149) | Local ip address | 192.168.100.144 |
7 minutes ago | Gateway | 0 | rtt (577) | D-Bus Round-trip time | 908 ms |
24 minutes ago | Gateway | 0 | au (150) | Auto update | Check |
24 minutes ago | Gateway | 0 | ut (151) | Update to | Official release |
24 minutes ago | Gateway | 0 | us (558) | Update status | Idle |
24 minutes ago | Gateway | 0 | fr (278) | Free space rootfs | 51895300 B |
24 minutes ago | Gateway | 0 | fd (279) | Free space data | 999559000 B |
24 minutes ago | Gateway | 0 | rwgm (582) | Run withoud grid meter | Yes |
24 minutes ago | Gateway | 0 | vl (256) | VRM Log mode | Enabled |
7 minutes ago | Gateway | 0 | TO (216) | VRM Log time offset | 1 s |
24 minutes ago | Gateway | 0 | sl (255) | VRM Log interval | 60 s |
24 minutes ago | Gateway | 0 | rdm (481) | VRM Log ram disk mode | normal |
24 minutes ago | Gateway | 0 | al (257) | User access level | User and installer |
24 minutes ago | Gateway | 0 | mb (258) | Modbus TCP service | Off |
24 minutes ago | Gateway | 0 | mql (572) | MQTT Local (https) | Off |
24 minutes ago | Gateway | 0 | mqli (573) | MQTT Local (http) | Off |
24 minutes ago | Gateway | 0 | tw (250) | Two way communication | On |
24 minutes ago | Gateway | 0 | dm (262) | Demo modus on/off | Off |
24 minutes ago | Gateway | 0 | tz (266) | Time zone | (removed for privacy) |
7 minutes ago | Gateway | 0 | H4bs (332) | ESS battery life state | BL Disabled (Low SoC) |
24 minutes ago | Gateway | 0 | bol (454) | DVCC | 1 |
7 minutes ago | Gateway | 0 | H4as (333) | ESS battery life SOC limit | 40.0 % |
24 minutes ago | Gateway | 0 | H4ms (334) | ESS Minimum SOC (unless grid fails) | 30.0 % |
7 minutes ago | Gateway | 0 | sca (469) | ESS Scheduled Charging | Not active |
24 minutes ago | Gateway | 0 | Vl (269) | VNC Local | Enabled |
24 minutes ago | Gateway | 0 | Vi (270) | VNC Internet | Enabled |
24 minutes ago | Gateway | 0 | sb (261) | Battery monitor setting | com.victronenergy.battery/260 |
7 minutes ago | Gateway | 0 | abs (263) | Active battery service | com.victronenergy.battery/260 |
24 minutes ago | Gateway | 0 | shd (253) | Has DC system | No |
24 minutes ago | Gateway | 0 | mfp (595) | Maximum configured feed-in power | -1 W |
24 minutes ago | Gateway | 0 | si1 (251) | AC Input 1 | Grid |
24 minutes ago | Gateway | 0 | si2 (252) | AC Input 2 | Not available |
24 minutes ago | Gateway | 0 | shao (560) | Has AC out system | Yes |
Gateway | 0 | lt (4) | Latitude | (removed for privacy) | |
Gateway | 0 | lg (5) | Longitude | (removed for privacy) |
|
24 minutes ago | Gateway | 0 | nr (692) | NodeRed | Off |
24 minutes ago | Gateway | 0 | sk (693) | SignalK | Off |
24 minutes ago | Gateway | 0 | H4of (741) | Feed excess DC-coupled PV into the grid | Off |
24 minutes ago | Gateway | 0 | H4pf (742) | Feed AC-coupled PV into the grid | Off |
24 minutes ago | Gateway | 0 | umc (743) | DVCC user configured maximum charge current | 140.0 A |
24 minutes ago | Gateway | 0 | umv (744) | DVCC user configured maximum charge voltage | 0.00 V |
7 minutes ago | Gateway | 0 | hp (470) | Hung processes | 0 |
7 minutes ago | Gateway | 0 | zp (479) | Zombie processes | 0 |
24 minutes ago | Gateway | 0 | dps (480) | Data partition status | fine |
24 minutes ago | Gateway | 0 | guiHash (1283) | GUI Hash for Remote Console | 0 |
24 minutes ago | Gateway | 0 | H4M (1042) | How ESS Multiphase regulation is done | Individual phase |
24 minutes ago | Gateway | 0 | H4sp (1174) | Grid setpoint | 150 W |
7 minutes ago | Gateway | 0 | ssl (1175) | Active SOC Limit | 30 % |
7 minutes ago | Gateway | 0 | cRelay (306) | Relay 1 state | Open |
7 minutes ago | Gateway | 0 | cRelay1 (335) | CCGX Relay 2 state | Open |
24 minutes ago | Gateway | 0 | rf0 (1046) | Relay 1 function | Alarm relay |
24 minutes ago | Gateway | 0 | rf1 (1047) | Relay 2 function | Manual |
24 minutes ago | Gateway | 0 | dem (1270) | Whether system accepts Dynamic ESS instructions. | Off |
24 minutes ago | Gateway | 0 | dems (1275) | Minimum battery SOC below which selling always stops | 20.0 % |
24 minutes ago | Gateway | 0 | dec (1289) | Dynamic ESS battery capacity | 0.00 kWh |
7 minutes ago | Gateway | 0 | des (1272) | Actual working state of Dynamic ESS | Off |
7 minutes ago | Gateway | 0 | dee (1290) | Dynamic ESS error code | No Error |
7 minutes ago | Gateway | 0 | Gt (1018) | Accumulated time for generic Generator | 0 |
7 minutes ago | VE.Bus System | 261 | ePR (519) | Phase rotation | Ok |
7 minutes ago | VE.Bus System | 261 | rt (581) | Waiting to perform relay test | OK |
24 minutes ago | VE.Bus System | 261 | vmk2 (6) | mk2 version | 1170216 |
24 minutes ago | VE.Bus System | 261 | pmk2 (356) | Mk2 product name | MK3 |
24 minutes ago | VE.Bus System | 261 | vvv (264) | VE.Bus firmware version | 502 |
24 minutes ago | VE.Bus System | 261 | vvp (265) | VE.Bus product id | 2623 |
24 minutes ago | VE.Bus System | 261 | vid (272) | VE.Bus ShortIDs | Two units configured in parallel |
24 minutes ago | VE.Bus System | 261 | vmc (316) | VE.Bus connection | VE.Bus |
7 minutes ago | VE.Bus System | 261 | IV1 (8) | Input voltage phase 1 | 244.9 V |
24 minutes ago | VE.Bus System | 261 | vcn (1167) | VE.Bus custom name | |
7 minutes ago | VE.Bus System | 261 | II1 (11) | Input current phase 1 | 3.7 A |
7 minutes ago | VE.Bus System | 261 | IF1 (14) | Input frequency 1 | 50.10 Hz |
7 minutes ago | VE.Bus System | 261 | IP1 (17) | Input power 1 | 517 W |
7 minutes ago | VE.Bus System | 261 | OV1 (20) | Output voltage phase 1 | 244.9 V |
7 minutes ago | VE.Bus System | 261 | OI1 (23) | Output current phase 1 | 2.2 A |
7 minutes ago | VE.Bus System | 261 | OF (26) | Output frequency | 50.0 Hz |
7 minutes ago | VE.Bus System | 261 | OP1 (29) | Output power 1 | 471 W |
7 minutes ago | VE.Bus System | 261 | CV (32) | Voltage | 52.24 V |
7 minutes ago | VE.Bus System | 261 | CI (33) | Current | 0.1 A |
24 minutes ago | VE.Bus System | 261 | PC (34) | Phase count | 1 |
7 minutes ago | VE.Bus System | 261 | AI (35) | Active input | AC Input 1 |
7 minutes ago | VE.Bus System | 261 | AILIM (27) | Active input current limit | 16.00 A |
7 minutes ago | VE.Bus System | 261 | vIL1 (1168) | AC Input 1 Current Limit | 16.00 A |
24 minutes ago | VE.Bus System | 261 | vIA1 (1170) | AC Input 1 Current Limit Adjustable | Adjustable |
2023-03-18 14:29:11 | VE.Bus System | 261 | VSH (240) | VE.Bus hidden SOC | 94.0 % |
7 minutes ago | VE.Bus System | 261 | S (40) | VE.Bus state | Bulk |
7 minutes ago | VE.Bus System | 261 | ERR (41) | VE.Bus Error | No error |
7 minutes ago | VE.Bus System | 261 | s (79) | Switch Position | On |
7 minutes ago | VE.Bus System | 261 | dPV (388) | Disable PV inverter | PV enabled |
24 minutes ago | VE.Bus System | 261 | sa (1106) | VE.Bus Switch Position Adjustable | Mode is adjustable |
7 minutes ago | VE.Bus System | 261 | eT (42) | Temperature | Ok |
7 minutes ago | VE.Bus System | 261 | eL (43) | Low battery | Ok |
7 minutes ago | VE.Bus System | 261 | eO (44) | Overload | Ok |
7 minutes ago | VE.Bus System | 261 | eTS (389) | Temperatur sensor alarm | Ok |
7 minutes ago | VE.Bus System | 261 | aps1 (280) | Hub4 power setpoint phase 1 | 472 W |
7 minutes ago | VE.Bus System | 261 | eVS (390) | Voltage sensor alarm | Ok |
7 minutes ago | VE.Bus System | 261 | H4S (284) | Hub4 sustain | Off |
7 minutes ago | VE.Bus System | 261 | Hcsp (396) | Charge voltage setpoint | 61.60 V |
7 minutes ago | VE.Bus System | 261 | t1 (317) | Energy AcIn1 to Inverter | 0.00 kWh |
7 minutes ago | VE.Bus System | 261 | t2 (318) | Energy ACIn2 to Inverter | 0.00 kWh |
7 minutes ago | VE.Bus System | 261 | t3 (319) | Energy ACIn1 to AcOut | 0.67 kWh |
7 minutes ago | VE.Bus System | 261 | t4 (320) | Energy ACIn2 to AcOut | 0.00 kWh |
7 minutes ago | VE.Bus System | 261 | t5 (321) | Energy Inverter to AcIn1 | 0.00 kWh |
7 minutes ago | VE.Bus System | 261 | t6 (322) | Energy Inverter to AcIn2 | 0.00 kWh |
7 minutes ago | VE.Bus System | 261 | t7 (323) | Energy AcOut to AcIn1 | 0.00 kWh |
7 minutes ago | VE.Bus System | 261 | t8 (324) | Energy AcOut to AcIn2 | 0.00 kWh |
7 minutes ago | VE.Bus System | 261 | t9 (325) | Inverter To AcOut | 0.07 kWh |
7 minutes ago | VE.Bus System | 261 | t10 (326) | AcOut to Inverter | 0.00 kWh |
24 minutes ago | VE.Bus System | 261 | asT0 (357) | Device 0 assistant list | 184 |
24 minutes ago | VE.Bus System | 261 | asT3 (360) | Device 3 assistant list | 184 |
7 minutes ago | VE.Bus System | 261 | vbc (392) | VE.Bus BMS allows battery to be charged | Yes |
7 minutes ago | VE.Bus System | 261 | vbd (393) | VE.Bus BMS allows battery to be discharged | Yes |
24 minutes ago | VE.Bus System | 261 | vbx (394) | VE.Bus BMS is expected | No |
7 minutes ago | VE.Bus System | 261 | vbe (395) | VE.Bus BMS error | No |
7 minutes ago | VE.Bus System | 261 | eR (523) | High DC Ripple | Ok |
7 minutes ago | VE.Bus System | 261 | eT1 (344) | Temperature L1 | Ok |
7 minutes ago | VE.Bus System | 261 | eL1 (345) | Low battery L1 | Ok |
7 minutes ago | VE.Bus System | 261 | eO1 (346) | Overload L1 | Ok |
7 minutes ago | VE.Bus System | 261 | eR1 (347) | High DC Ripple L1 | Ok |
7 minutes ago | VE.Bus System | 261 | eT2 (348) | Temperature L2 | Ok |
7 minutes ago | VE.Bus System | 261 | eL2 (349) | Low battery L2 | Ok |
7 minutes ago | VE.Bus System | 261 | eO2 (350) | Overload L2 | Ok |
7 minutes ago | VE.Bus System | 261 | eR2 (351) | High DC Ripple L2 | Ok |
7 minutes ago | VE.Bus System | 261 | eT3 (352) | Temperature L3 | Ok |
7 minutes ago | VE.Bus System | 261 | eL3 (353) | Low battery L3 | Ok |
7 minutes ago | VE.Bus System | 261 | eO3 (354) | Overload L3 | Ok |
7 minutes ago | VE.Bus System | 261 | eR3 (355) | High DC Ripple L3 | Ok |
7 minutes ago | VE.Bus System | 261 | vcs (557) | Charge state | Bulk |
7 minutes ago | VE.Bus System | 261 | vbl (1267) | BMS lost | No alarm |
7 minutes ago | VE.Bus System | 261 | q0 (544) | VE.Bus netw. error count - unit 1 | 2 |
7 minutes ago | VE.Bus System | 261 | q3 (547) | VE.Bus netw. error count - unit 4 | 1 |
7 minutes ago | VE.Bus System | 261 | eV (649) | High DC Voltage | OK |
7 minutes ago | VE.Bus System | 261 | eC (650) | High DC Current | OK |
7 minutes ago | VE.Bus System | 261 | v0 (651) | Device 0 High DC Voltage | 0 |
7 minutes ago | VE.Bus System | 261 | v3 (655) | Device 3 High DC Voltage | 0 |
7 minutes ago | VE.Bus System | 261 | d0 (664) | Device 0 High DC Current | 0 |
7 minutes ago | VE.Bus System | 261 | d3 (667) | Device 3 High DC Current | 0 |
7 minutes ago | VE.Bus System | 261 | ia (677) | Ignore AC input | Not ignored |
24 minutes ago | VE.Bus System | 261 | vs0 (1107) | Serial number of 1st device | (removed for privacy) |
24 minutes ago | VE.Bus System | 261 | vs3 (1122) | Serial number of 4th device | (removed for privacy) |
38 minutes ago | VE.Bus System | 261 | ns0 (678) | Interface protection log 0 | (1000) |
7 minutes ago | VE.Bus System | 261 | p0 (719) | Device 0 Power-pack pre-overload | 0 |
7 minutes ago | VE.Bus System | 261 | p3 (722) | Device 3 Power-pack pre-overload | 0 |
7 minutes ago | VE.Bus System | 261 | H4f1 (732) | L1 Frequency Variation | OK |
7 minutes ago | VE.Bus System | 261 | H4l1 (1039) | Max Feedin Power L1 | 65532 W |
7 minutes ago | VE.Bus System | 261 | vu (1176) | Uptime of the 1st device | 1740 s |
7 minutes ago | VE.Bus System | 261 | vu3 (1179) | Uptime of the 4th device | 1740 s |
7 minutes ago | VE.Bus System | 261 | vr0 (1138) | VE.Bus Voltage ripple - unit 1 | 0.00 V |
7 minutes ago | VE.Bus System | 261 | vr3 (1141) | VE.Bus Voltage ripple - unit 4 | 0.00 V |
7 minutes ago | VE.Bus System | 261 | vt0 (1150) | VE.Bus Terminal voltage- unit 1 | 52.12 V |
7 minutes ago | VE.Bus System | 261 | vt3 (1153) | VE.Bus Terminal voltage - unit 4 | 52.34 V |
7 minutes ago | VE.Bus System | 261 | vu0 (1162) | VE.Bus sense voltage - unit 1 | 52.24 V |
24 minutes ago | Battery Monitor | 260 | Bcn (585) | Battery custom name | |
24 minutes ago | Battery Monitor | 260 | BM (45) | Model | 203 |
24 minutes ago | Battery Monitor | 260 | BV (46) | Firmware version | v3.11 |
24 minutes ago | Battery Monitor | 260 | BSN (114) | Serial Number | (removed for privacy) |
7 minutes ago | Battery Monitor | 260 | V (47) | Voltage | 52.25 V |
7 minutes ago | Battery Monitor | 260 | I (49) | Current | 0.10 A |
7 minutes ago | Battery Monitor | 260 | CE (50) | Consumed Amphours | -206.70 Ah |
7 minutes ago | Battery Monitor | 260 | SOC (51) | State of charge | 29.0 % |
7 minutes ago | Battery Monitor | 260 | TTG (52) | Time to go | 0.00 h |
7 minutes ago | Battery Monitor | 260 | AL (119) | Low voltage alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | AH (120) | High voltage alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | ALS (121) | Low starter-voltage alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | AHS (122) | High starter-voltage alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | ASoc (123) | Low state-of-charge alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | ALT (124) | Low battery temperature alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | AHT (125) | High battery temperature alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | AM (126) | Mid-voltage alarm | No alarm |
7 minutes ago | Battery Monitor | 260 | Relay (54) | Relay status | Open |
24 minutes ago | Battery Monitor | 260 | H1 (55) | Deepest discharge | -218.50 Ah |
10 minutes ago | Battery Monitor | 260 | H2 (56) | Last discharge | -206.70 Ah |
24 minutes ago | Battery Monitor | 260 | H3 (57) | Average discharge | -105.90 Ah |
24 minutes ago | Battery Monitor | 260 | H4 (58) | Charge cycles | 164.00 |
24 minutes ago | Battery Monitor | 260 | H5 (59) | Full discharges | 0.00 |
10 minutes ago | Battery Monitor | 260 | H6 (60) | Total Ah drawn | -28701.30 Ah |
24 minutes ago | Battery Monitor | 260 | H7 (61) | Minimum voltage | 40.89 V |
24 minutes ago | Battery Monitor | 260 | H8 (62) | Maximum voltage | 64.76 V |
7 minutes ago | Battery Monitor | 260 | H9 (63) | Time since last full charge | 1.20 |
24 minutes ago | Battery Monitor | 260 | H10 (64) | Automatic syncs | 116.00 |
24 minutes ago | Battery Monitor | 260 | H11 (65) | Low voltage alarms | 0.00 |
24 minutes ago | Battery Monitor | 260 | H12 (66) | High voltage alarms | 0.00 |
10 minutes ago | Battery Monitor | 260 | H21 (244) | Discharged Energy | 1512.81 kWh |
24 minutes ago | Battery Monitor | 260 | H22 (245) | Charged Energy | 1628.10 kWh |
7 minutes ago | Battery Monitor | 260 | dH21 (338) | Discharged Energy delta | 0.05 kWh |
3 hours ago | Battery Monitor | 260 | dH22 (339) | Charged Energy delta | 0.01 kWh |
7 minutes ago | Solar Charger | 1 | ScOR (583) | Solar charger off reason | No input power (1) |
24 minutes ago | Solar Charger | 1 | Sccn (586) | Solar charger custom name | (removed for privacy) |
24 minutes ago | Solar Charger | 1 | ScM (106) | Solarcharger model | a115 |
24 minutes ago | Solar Charger | 1 | ScVt (80) | Solar charger version | v3.14 |
24 minutes ago | Solar Charger | 1 | ScSN (118) | Solar charger serial number | (removed for privacy) |
7 minutes ago | Solar Charger | 1 | ScV (81) | Voltage | 52.2 V |
24 minutes ago | Solar Charger | 1 | Scvs (1105) | Voltage setting | 48 |
7 minutes ago | Solar Charger | 1 | ScI (82) | Current | 0.0 A |
7 minutes ago | Solar Charger | 1 | ScW (107) | Battery watts | 0 W |
7 minutes ago | Solar Charger | 1 | SLs (241) | Load state | On |
7 minutes ago | Solar Charger | 1 | Scs (84) | Charger on/off | On |
7 minutes ago | Solar Charger | 1 | ScS (85) | Charge state | Off |
7 minutes ago | Solar Charger | 1 | PVV (86) | PV voltage | 0.7 V |
7 minutes ago | Solar Charger | 1 | PVP (442) | PV power | 0 W |
7 minutes ago | Solar Charger | 1 | ScMm (518) | MPPT State | Off |
7 minutes ago | Solar Charger | 1 | SRelay (90) | Relay on the charger | Open |
7 minutes ago | Solar Charger | 1 | SceL (92) | Low batt. voltage alarm | No alarm |
7 minutes ago | Solar Charger | 1 | SceH (93) | High batt. voltage alarm | No alarm |
7 minutes ago | Solar Charger | 1 | YT (94) | Yield today | 2.23 kWh |
7 minutes ago | Solar Charger | 1 | MCPT (95) | Maximum charge power today | 609 W |
7 minutes ago | Solar Charger | 1 | YY (96) | Yield yesterday | 13.38 kWh |
7 minutes ago | Solar Charger | 1 | MCPY (97) | Maximum charge power yesterday | 2508 W |
7 minutes ago | Solar Charger | 1 | ScERR (98) | Error code | No error |
7 minutes ago | Solar Charger | 1 | YU (285) | User yield | 1875.86 kWh |
4 hours ago | Solar Charger | 1 | dYU (340) | User yield delta | 0.01 kWh |
7 minutes ago | Solar Charger | 2 | ScOR (583) | Solar charger off reason | No input power (1) |
24 minutes ago | Solar Charger | 2 | Sccn (586) | Solar charger custom name | (removed for privacy) |
24 minutes ago | Solar Charger | 2 | ScM (106) | Solarcharger model | a115 |
24 minutes ago | Solar Charger | 2 | ScVt (80) | Solar charger version | v3.14 |
24 minutes ago | Solar Charger | 2 | ScSN (118) | Solar charger serial number | (removed for privacy) |
7 minutes ago | Solar Charger | 2 | ScV (81) | Voltage | 52.2 V |
24 minutes ago | Solar Charger | 2 | Scvs (1105) | Voltage setting | 48 |
7 minutes ago | Solar Charger | 2 | ScI (82) | Current | 0.0 A |
7 minutes ago | Solar Charger | 2 | ScW (107) | Battery watts | 0 W |
7 minutes ago | Solar Charger | 2 | SLs (241) | Load state | On |
7 minutes ago | Solar Charger | 2 | Scs (84) | Charger on/off | On |
7 minutes ago | Solar Charger | 2 | ScS (85) | Charge state | Off |
7 minutes ago | Solar Charger | 2 | PVV (86) | PV voltage | 0.9 V |
7 minutes ago | Solar Charger | 2 | PVP (442) | PV power | 0 W |
7 minutes ago | Solar Charger | 2 | ScMm (518) | MPPT State | Off |
7 minutes ago | Solar Charger | 2 | SRelay (90) | Relay on the charger | Open |
7 minutes ago | Solar Charger | 2 | SceL (92) | Low batt. voltage alarm | No alarm |
7 minutes ago | Solar Charger | 2 | SceH (93) | High batt. voltage alarm | No alarm |
7 minutes ago | Solar Charger | 2 | YT (94) | Yield today | 2.17 kWh |
7 minutes ago | Solar Charger | 2 | MCPT (95) | Maximum charge power today | 597 W |
7 minutes ago | Solar Charger | 2 | YY (96) | Yield yesterday | 12.49 kWh |
7 minutes ago | Solar Charger | 2 | MCPY (97) | Maximum charge power yesterday | 2344 W |
7 minutes ago | Solar Charger | 2 | ScERR (98) | Error code | No error |
7 minutes ago | Solar Charger | 2 | YU (285) | User yield | 1822.64 kWh |
4 hours ago | Solar Charger | 2 | dYU (340) | User yield delta | 0.01 kWh |
7 minutes ago | System overview | 0 | i1 (564) | AC Consumption on Input L1 | 0 W |
7 minutes ago | System overview | 0 | o1 (567) | AC Consumption on Output L1 | 471 W |
21 minutes ago | System overview | 0 | st (570) | System type | ESS |
7 minutes ago | System overview | 0 | ss (571) | System state | Bulk |
7 minutes ago | System overview | 0 | evc (578) | Effective charge voltage | 61.6 V |
2 hours ago | System overview | 0 | Gb (100) | Grid to battery | 0.02 kWh |
7 minutes ago | System overview | 0 | Gc (101) | Grid to consumers | 0.36 kWh |
4 hours ago | System overview | 0 | Pb (102) | PV to battery | 0.02 kWh |
2023-10-15 12:00:12 | System overview | 0 | Pg (103) | PV to grid | 0.04 kWh |
7 minutes ago | System overview | 0 | ssls (472) | #1 Low SOC; discharge disabled | On |
7 minutes ago | System overview | 0 | ssbl (473) | #2 BatteryLife is active | Off |
7 minutes ago | System overview | 0 | ssdc (475) | #3 Charge disabled by BMS | Off |
7 minutes ago | System overview | 0 | ssdd (474) | #4 Discharge disabled by BMS | Off |
7 minutes ago | System overview | 0 | sssc (476) | #5 Slow charge is active | Off |
7 minutes ago | System overview | 0 | ssuc (477) | #6 Charge disabled by user setting | Off |
7 minutes ago | System overview | 0 | ssud (478) | #7 Discharge disabled by user setting | Off |
4 hours ago | System overview | 0 | Pc (104) | PV to consumers | 0.02 kWh |
7 minutes ago | System overview | 0 | Bc (105) | Battery to consumers | 0.04 kWh |
2023-10-15 08:00:28 | System overview | 0 | Bg (108) | Battery to grid | 0.02 kWh |
7 minutes ago | System overview | 0 | Pdc (113) | PV - DC-coupled | 0 W |
7 minutes ago | System overview | 0 | a1 (131) | AC Consumption L1 | 471 W |
7 minutes ago | System overview | 0 | g1 (134) | Grid L1 | 511 W |
7 minutes ago | System overview | 0 | bv (143) | Voltage | 52.25 V |
7 minutes ago | System overview | 0 | bc (147) | Current | 0.00 A |
7 minutes ago | System overview | 0 | vc (153) | VE.Bus charge current | 0.0 A |
7 minutes ago | System overview | 0 | bp (243) | Battery Power | 0 W |
7 minutes ago | System overview | 0 | vp (254) | VE.Bus charge power | 40 W |
7 minutes ago | System overview | 0 | bs (144) | Battery SOC | 29.0 % |
7 minutes ago | System overview | 0 | bst (215) | Battery state | idle |
7 minutes ago | System overview | 0 | ba (145) | Battery Consumed Amphours | -206.70 Ah |
8 minutes ago | System overview | 0 | bt (146) | Battery Time to Go | 240.00 h |
7 minutes ago | System overview | 0 | Amb (579) | DVCC Multiple batteries alarm | No alarm |
7 minutes ago | System overview | 0 | Af (580) | GX Error #48 DVCC with incompatible firmware | No alarm |
7 minutes ago | System overview | 0 | H4m (676) | No grid meter alarm | OK |
15 minutes ago | System overview | 0 | To (531) | Time off | 51.00 s |
7 minutes ago | System overview | 0 | Tg (533) | Time grid | 553.00 s |
35 minutes ago | System overview | 0 | Ti (534) | Time inverting | 511.00 s |
7 minutes ago | System overview | 0 | AIS (471) | AC-Input | Grid |
7 minutes ago | System overview | 0 | ic0 (825) | AC Input 1 connected | Connected |
7 minutes ago | System overview | 0 | id0 (827) | AC Input 1 device instance | 261 |
7 minutes ago | System overview | 0 | vi0 (918) | AC Input 1 VRM device instance | 261 |
7 minutes ago | System overview | 0 | ist0 (829) | AC Input 1 service type | vebus |
7 minutes ago | System overview | 0 | is0 (831) | AC Input 1 source | Grid |
7 minutes ago | System overview | 0 | ini (833) | Number of AC Inputs | 1 |
7 minutes ago | System overview | 261 | Agl (559) | Grid alarm | Grid ok |