I am attempting to get the "/Settings/Cgwacs/MaxDischargePower" value from the Modbus but I can find the Slave address for the Register 2704. I have tried 100, 242, 243, 245 but with no luck.
Any help with the correct address?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I am attempting to get the "/Settings/Cgwacs/MaxDischargePower" value from the Modbus but I can find the Slave address for the Register 2704. I have tried 100, 242, 243, 245 but with no luck.
Any help with the correct address?
I needed to upgrade to the newest firmware and then you will find the data on 100
I'm trying to set this value to "-1" via Modbus TCP so that my Venus has the "No Limit" setting for the inverter power. As per https://www.victronenergy.com/live/ess:ess_mode_2_and_3 this should be possible. I can set any other positive value via the Modbus, but not "-1". Any suggestions how I can do this via Modbus?
Currently I'm simply setting the value to "0" when I don't want to discharge the battery and to "7000" if I want to allow normal discharging. My system can do max. 7200W. It still would be nice to be able to do this "cleanly".