I had my system professionally installed about 2 years ago. On the most part the system has worked without problems until recently.
Over the last couple of months I’ve noticed the MultiPlus is only charging the batteries from solar but when I turn my generator on it doesn’t charge from that. I’ll see power going to both legs but it is not charging the batteries.
In the past I’ve had problems with the Digital Multi Control after the batteries have gone to 0% where the controller is stuck at 16 amps charge rate on the display. The only way to resolve it is by unplugging it and plugging it back in.
So I’m wondering if the Digital Multi Control is causing this problem too. I haven’t unplugged it yet as I wanted to run this by the community first.
System components
MultiPlus-II 12/3000/120-50 2x120V
Digital Multi Control 200/200A
SmartShunt 500A/50mV
Blue SolarSmart MPPT 150/85-Tr
Cerbo GX & Touch 50 monitor
5 - BattleBorn GC2 batteries
All components have the latest firmware.
In this picture, under the Generator, it used to see say 2,400W on L1 when the batteries are charging.