Hi Crew..... I've been getting Error #29 Overcharge Protection events whenever I turn off "DC-Coupled PV - Feed in excess" within my ESS environment.
The Charge Voltage is seen to spike, then the Overprotection occurs and the MPPT stops charging and needs to be restarted after the event is cleared. Note: ESS is set to "Keep Battery's Charged".
See attached VRM Charts etc...
Is this a case of the MPPT not ramping down quick enough for the BMS, and therefore the BMS triggering a high cell voltage or something ? If so.... How do I prevent or negate this in the future ? (besides just never turning off 'Grid feed-in')
My panels Voc are well within voltage specs for the MPPT, so I don't believe this is a factor.
In times of excess solar being fed back to my home and grid, I sometimes need to limit the power and/or turn off this feature due to limited AC cable size feeding back from my Multiplus to my MCB and grid export limits etc.
What are the recommended BMS settings for Cell OV Alarm / Protect / Release & Delay time ?
Setup>>
Multiplus II 48v 8K/110 230v (via VE.Bus)
DC-Coupled 14x Kookuburra 415w Panels (5.81 kW) (7S2P)
MPPT RS 450/100 Tr (via VE.Direct)
2X Parallel BSL LiFePo4 48v 100 Ah 5.12 kWh Batteries (via CAN-Bus)
Cerbo GX
Configured on a rear studio (with sub board) and grid connected via the main switchboard using the Victron Energy Meter (ET112) between grid / MCB
Also on the main switchboard is an AC-Coupled GoodWe MS-10kW Inverter (with HomeKit Smart Meter) fed by 18x 440w Jinko Panels (7.92kW) (9S2P)
P.S. My current charge voltage is set to 56.8v as I'm attempting to top balance the new BSL battery packs, and not as a permanent charge voltage (normally 55.2v - as within my current ESS environment there is no such thing as bulk/abs/float of course)