I've had single phase single multiplus ESS for 6months running fine.
I use external et112 to monitor grid and most of my loads are on grid side (ACIN)
this weekend I added a second multiplus in parallel (equal wire lengths, same model etc)
All works perfect at night and under higher loads but on lower load it uses grid.
To me this screams peak shaving. And I did reduce the dvcc cirrent limit and added limit inverter power in ess while testing .
I've now removed those limits to try resolve the problem.
Anyone think of any other cause or is it likely peak shaving? Anything in veconfig I've maybe missed?
I have schedule charging overnight due to cheap power hence grid usage overnight but doesn't explain grid usage during the day starting st 9am ish.
Higher loads seem to sort the probelm which makes me think peak shaving but could it be an anything else?