I have a strange issue with a SmartSolar MPPT 100/50.
Each morning (and evening) the status is extreme frequent switchin in between "bulk" and "off".
The problem is, that sometimes the MPPT is stuck in Off mode,
while the other MPPT's running well.
Screenshot is from a sunny day, no clouds on sky.
When this issue happen, that the MPPT is stuck in off mode,
I have to remotely login and Switch Off / Switch On the MPPT Charger from his Settings.
But this workaround means I have to manually control this MPPT3 100/50 each morning ...
... here:
Within the same time another MPPT1 100/30 string (same panel orientation) don't show the issue.
What I have tested so far ?
I have replaced the faulty MPPT3 100/50 against another spare (older) Smartsolar MPPT 100/30, all is fine !
However the spare MPPT 100/30 which I have is a bit undersized for this string, not much, but few Amp's on a sunny day. That's why I want to use the 100/50
Then I have tested another (newer) SmartSolar 150/45 ... curious same issue with the (newer) 100/50. Both newer (Problem-) Smartsolar MPPTs have a Serial Number starting with HQ23...
Then I swapped the other working MPPT1 100/30 to the "problem string" ... no issue as well, all is fine with the String 3.
So the problem seems definitive with the MPPT 100/50, not the cables, not fuses, battery ...
... as far as I see.
The Firmware is everywhere the same on latest. v1.61
MPPT Rotary Switch is at position 7 (LifePo4) (all MPPTs) and I use the default settings for Victron's Lifepo4 from the App.
All MPPTs are networked over BT.
And all MPPTs and the SmartBMV 712 are connected to a Raspi 3 (Firmware v2.89) over USB.(VE.direct USB cables).
DVCC is disabled.
Remote Console say ... Not networked for all MPPTs
Does this make a difference to implement Networking some how ?
The only difference so far I see is ...
that my older MPPTs with Serial# HQ18 ... are always working perfect,
while any newer MPPT Models Serial# HQ23... not.
It's a island system, not connected to grid. (no such ESS setup).
I'm using a Phoenix Inverter and Victron LifePo4 Battery Bank managed with a Victron smallBMS.
No VE.can, no VE.bus.
Any ideas for another workaround, other then manually check each morning the bulk state ?