Fronius Symo Advnaced recognized as single phase on VRM.

Screenshot 2023-09-17 104304.pngScreenshot 2023-09-17 104320.pngScreenshot 2023-09-17 104401.pngI have recently installed 2 ESS three phase systems.

Both have a FRONIUS SYMO ADVANCED attached.

On both systems (all firmwares updated) the Symo is recognized as single phase.

The result is a terrible mess up with the readings! The inverter is also appearing as UNknown instead of Fronius. See the readings on the attached snapshot to see how the L1 readings are crazy...

Any ideas?

Fronius
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

samson avatar image samson commented ·

I am experiencing same issues, I will really appreciate your support.




settings2.pngsettings1.png


0 Likes 0 ·
settings1.png (41.2 KiB)
3 Answers
Vangelis Beligiannis avatar image
Vangelis Beligiannis answered ·

The solution is to configure SunSpec support on the PV-inverter. Log into the Fronius web interface. Go to the Modbus tab Set Data export via Modbus to tcp. set Sunspec Model Type to int + SF

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@Vangelis Beligiannis @Samson

Is modbus TCP enabled?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

samson avatar image samson commented ·
Modbus TCP Not Enable.
0 Likes 0 ·
samson avatar image samson commented ·

Modbus is not enable….

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ samson commented ·

@Samson

It is important for you to enable that on the fronius and the GX for it to work and be detected correctly

See Question 6

0 Likes 0 ·
Eugenio Velasco avatar image
Eugenio Velasco answered ·

Hi I have the same issue, 3 inverters Fronius Symo. The new Fronius Symo Advance it show as Unknown PV inverter, Damanager works correctly, 1700478509845.png

It seems to be an interpretation error , generated by Cerbo GX 1700479020783.png


One of another inverters shows as picture, and i didn't have to configurate anything more to reach this status.

1700479073482.png




1700478509845.png (23.6 KiB)
1700479020783.png (17.4 KiB)
1700479073482.png (23.4 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
As @Vangelis Beligiannis mentioned the sunspec has to enabled on the Fronius itself and modbus TCP.

Check your settings on the Fronius.


0 Likes 0 ·