question

carlosn avatar image
carlosn asked

Change the "Maximum Charge Power" through modbus

How do I change the Maximum Charge Power through modbus. The address I think is 2705. In the list the address 2705 is described as Ampreres in the ESS it is described as Watts. So I'm not sure it's the same. Someone can help me. I want to create an automation in Home Assistant to charge the battery at night, but I don't want it to charge at more than 1000W until it reaches a certain SOC. I would appreciate help. Thanks.

Modbus TCPhome assistantscheduled charge
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
lifeingalicia avatar image
lifeingalicia answered ·

Hi under DVCC it is in Amps Inverter is in watts

To test simply read in via modbus then change manually and read in again then you know you got the right one.


1696179706818.png


1696179706818.png (11.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.