Last night my CCGX upgraded to V2.32 and since then my battery parameters via the modbus registers 259, 261 and 266 (device instance 225) do no longer respond.
Is there a change in the modbus registers?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Last night my CCGX upgraded to V2.32 and since then my battery parameters via the modbus registers 259, 261 and 266 (device instance 225) do no longer respond.
Is there a change in the modbus registers?
I have noted the that all register addresses have changed to: address +1
Maybe a firmware bug?
Hi @KFarber and Juergen, there has been no change in addressing for said registers.
For details for changes made, see the Venus OS change log, available at https://professional.victronenergy.com.
For this part there is also source code available, see here: https://github.com/victronenergy/dbus_modbustcp/commits/master
v0.9.28 is shipping in Venus v2.32 and v2.33.
v0.9.26 is shipping in v2.31.
10 People are following this question.