Hello community,
I am runnig a MultiPlus II with Cerbero GX and SmartSolar 100/50 in ESS mode together with a Pylontec UP2400. In the first days I configured SoC minimum of 30% with battery life. After a few days the "actual SoC" rised to 45% and the battery low led was illuminated when the battery went low but no aural alarm was tripped. Discharging was also stopped at the given limits for battery life.
To have more usable capacity, I've lowered the SoC minimum to 25%. After a few days the "actual SoC" was lowered also to 25% due to good weather and in the first night, not only the battery low LED was lit, but also the aural alarm sounded.
Of course I can simply disable audible alarms or set the SoC limit back to 30%.
But having the same behavior as before would be nice. Can this be achieved by some configuration?
--