question

max-payne avatar image
max-payne asked

2 Phase ESS with Multiplus and Multiplus II

Victron states that for 2 phase ESS operation the power of the units has to match. So you cannot parallel a 3000VA and a 5000VA unit in a 2 phase setup.

Question: Is it supported to use say a Multiplus 48/5000/70 and a Multiplus-II 48/5000/70?
I am asking because VE.BUS system configuratior does not seem to differentiate anywhere so it might be possible or even supported?

Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

max-payne avatar image max-payne commented ·

Well that... Or a second GX device looking at its phase only but phases will drift.
No headache for household but could be for 3 phase devices.

0 Likes 0 ·