Multiplus II,
”Mains On” on
”Bulk” on
”inverter on” flashing.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
The unit is likely in bulk charge state and power assisting.
But a few more information about the system could help.
Mine is doing the same as the one in your distributor’s video https://www.youtube.com/watch?v=xHQGOfSGQd4
Please give us some more information about your system.
MultiPlus II, CerboGS, ESS, grid parallel, external current transformer, exactly the same as the one in the video, supplying a grid connected load and avoiding export.
On the GX, under device list the ve bus state should be shown there.
So, If I want to know what it is doing, and I look at its LEDs and BULK is lit, it could either be doing bulk charge, or it could be doing grid-tied inverting, it is almost impossible to tell unless I fetch my iPad, run the Victron connect app, change the source of my wi-fi and log in to the remote console.
Really?
I am very pleased that I installed analogue volt and current meters on the battery.
Well the GX is really designed to be used with a screen. And if you connect your GX to the wifi, the remote screen is available over the local network.
In fact you can use the ip address in a browser and skip the app completely.
The leds you described is usually when the inverter/solar is grid connected thr battery is in bulk state and the solar is aiding loads. So ESS.....Additional resources still need to be added for this topic