380VAC Output 3 phase quattro 8000

Hello,

I am setting up 3 phase system using victron Quattro 8000 with UPS function.


As per the manual the output voltage of each inverter is 230VAC, however in a 3 phase system the voltage is 380VAC.

I want to confirm the following points:

1- The inverter will adjust the phase to phase voltage to 380VAC by itself?

2- We have 3 phase motor load connected to the 3 phase inverters, when the power cut off, I am worried that the generated voltage by the inverter will have different phase sequence from the grid before interruption and this may cause the motor to run in different direction.

Please let me know if someone can help.


Thanks

Hisham

3 phaseups
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

The Quattro's can only be configured in a Star (Wye) configuration. 230V Phase to Neutral.

It is not possible to configure the Quattro's in a Delta configuration.