question

Gerrie Rossouw avatar image
Gerrie Rossouw asked

Compressor from Star to delta

Good day


We are about to install a three phase Victron system, the customer has a compressor which start the following way


Will this be an issue on the Victron side?


Regards

MultiPlus Quattro Inverter Chargervictron
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Gerrie Rossouw

You picture did not load.

Star delta start up is not a problem if the system is sized correctly.

Delta loads are not a problem.

0 Likes 0 ·
Gerrie Rossouw avatar image Gerrie Rossouw Alexandra ♦ commented ·
Apologies, the picture says the following " Motor starts running for 25 seconds, with start and switches to delta after 10 seconds"
0 Likes 0 ·
1 Answer
mvas avatar image
mvas answered ·

"Wye-Start" & "Delta-Run" is very common in 3 Phase.
A similar effect to a soft-starter.
Compressors are always an "issue", for any inverter.
The WYE connected inverters must be rated to handle the starting amps, for a short period.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.