question

Franklin Bravo avatar image
Franklin Bravo asked

Victron Quattro+Pylontech Force L1 System

I have a Victron+Pylontech backup system, which randomly without failures in the AC supply network, first the low voltage battery alarms appear, high discharge current and the entire system shuts down for 3 minutes. I understand that the BMS of the batteries is the one that controls the operation of the system. Is this true?

PylontechBattery Protectfault
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
tnt369 avatar image
tnt369 answered ·

First check the reason for the high discharge current.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Franklin Bravo avatar image
Franklin Bravo answered ·

There is no indication or cause of high current, no fault, no power consumption, no high temperature. This has occurred even under conditions of minimum consumption.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tnt369 avatar image
tnt369 answered ·

Please more information about your system (what components and how many, connect to grid ...).

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tnt369 avatar image
tnt369 answered ·

Have you seen this:

Pylontech Force L1 High discharge current alarm on low Load - Victron Community (victronenergy.com)


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Franklin Bravo avatar image
Franklin Bravo answered ·

Thank you for your valuable help, we updated the battery firmware and the fault disappeared. The update is done by Pylontech via the internet. We still do not know the technical reasons for this failure.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Victron Pylontech battery compatibility guide

Victron BatteryProtect product page

Faults with Victron equipment are best discussed directly with your dealer - this can be formalised with this support request form.