PV low amps / watts

At the CB in off position i am reading with multimeter approx 180 - 200v and 11amps, when the unit is on it reports similar voltage but watts are low @ 30w approx. I do not understand this as surely amps x volts = watts, so i should be getting 2000w - I have not setup the unit in terms of software yet.

I have 2 x 5 panels in a row unshaded, 3 are longi and are 370w and 2 are JA 380w, then the next string are all JA 380w. very little variation between longis. I have inline fuses 15a on each string and on the one with longi a shockty diode.

Series connected with parallel string wired to Y connectors so just a + and - before the main CB see below


I have checked for blown fuses and wires not connecting. Is it likely to be the 3 longi panels?

Am wondering if wired wrong, this is what I have wired the panels, note in the middle the + connects to the + of the beginning of the next string, the common connects similar (see blue line), then both 2 poles go to the circuit breaker before unit.


screenshot-20230713-092955-1.png2 strings of 10 panels in total



PV 3.8kw Offgrid: Victron EasySolar 2 GX 48v.35a with mppt 250/70 3000w

  1. Panels = 7 x JA SOLAR JM60S20 380/MR 380W VOC 41.62 V VMP 34.77 V ISC 11.47 A MP 10.93 A CLASS II MAX SYS 1000V, MAX AMP 20 TOTAL 3,8KW 3 x longi 370w similar to above.

  2. two strings 5 x 2 in series and wired series parallel, only one mppt and costly for another so all panels same direction height etc.PV Wiring = 6mm x 10m to inverter from shortest end 17m from last panel. 1 shocty diodes inline on string with 3 longi panels,

  3. 1000v/20a to prevent reverse polarity. Then 32a 1000v disconnect before going to inverter

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
mvas avatar image
mvas answered ·

Is the Battery Bank fully charged?
Post an image of your PV Configuration from 270/50 MPPT
Post an image of the Battery Status from 270/50 MPPT


If the Battery Bank needs Charging then ...
Remove the Schotky Diodes.
Remove the parallel connection.
Verify Voc and Isc on String #1
Connect only String #1 to the MPPT = Results?
Disconnect String #1 from the MPPT.
Verify Voc and Isc on String #2
Connect only String #2 to the MPPT = Results?

What are your results?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Andrew avatar image
Andrew answered ·

@mvas batteries are low. Will go through your suggestions, thanks