Which inverter for 48V 300Ah AGM batteries

I have 32 pieces of 12V 56Ah AGM batteries here. If I discharge the batteries to 70% I would have 48V 300Ah. I would like to connect this to a Victron multiplus-ii gx 48/5000 inverter. Apart from the installation, I have 6300Wp of solar panels. Every year I inject approx 3500 kWh on the grid. That's why I want a system to store my own energy. The question is would I use all the batteries? So 8 sets of 48V together 300Ah. Total 15 kWh or should I use a few batteries less because I only have 6300 Wp of solar panels? Which Victron multiplus-ii gx should I buy, a 3000 or a 5000? If the batteries have lost their capacity, it is the intention to replace them with LifeP04 cells.


Sunnybeam

Multiplus-IISolar PanelAGM Battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
mvas avatar image
mvas answered ·

Do you actually plan to connect 4 AGM batteries in series, and then connect 8 Banks in parallel?
What is the plan to keep all 32 batteries equally changed / balanced?

14,400 Watt-Hour = 48 Volts x 300 Ah
4.8 Hours runtime at max power = 14,400 / 3,000 watts
2.9 Hours runtime at max power = 14,400 / 5,000 watts

Will you have enough Sun-Hours, in the winter, to recharge the AGM battery bank from 70% SOC?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sunnybeam avatar image
sunnybeam answered ·

Thank you mvas for your message. In theory, the plan is to connect 4 AGM batteries in series, and then connect 8 Banks in parallel. But I can also connect less. In winter I will not be able to charge the batteries if there is no sun, even on a sunny day in December I only have 8 kWh of solar panels. So not enough to fully charge the batteries with the solar panels.n.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

Ypu cant leave agms just sitting they must be maintained.

It is better to have a big bank and not cycle only some of them to a low soc. (They will then mis match and be aged faster than the other batteries) the other batteries will self dicharge and be in bad condition.

What @mvas is saying is you will need a way to balance the different batteries in the bank and maintain them. You will also need to wire them in a way that they all current share well or some will work harder than others and also age faster.

Make sure you also have a 12v charger and good digital multimeter to keep checking them. Rotating batteries in the bank as well will be a good plan. And buy battery balancers.