I need help with my generator and my multiplus. I'll give as much detail as I can.
I've got 9 solar panels at 400 watts each
6 are run into a SmartSolar HQ1913LXE7V MPPT 250/100
3 are run into a SmartSolar HQ1930LHU7E MPPT 150/60
I'm running 4 Tesla battery modules
My inverter is a Mutiplus 24/3000/70
My generator is a Champion dual fuel 3400/3060
What I want is the generator to help out on hot days.
For example I'm pulling in about 2000watts of solar
I've got a 1500 watt load going with the air conditioner, etc.
What I would like is to run the load on the generator and let the solar just pour into the batteries. It seems like it happens everytime the load increases. I've got a soft start on my AC, but when the compressor kicks on, the passthru kicks off and just the inverter is running. It says -80a while the load is running on the inverter screen.
My Grid settings are as follows: AC low voltage disconnect = 90V, AC low voltage connect = 91V, AC high voltage connect = 135V, and AC high voltage disconnect = 140V.
I've fiddled with the power assist boost settings, UPS settings, ground relay, and dynamic current limit to no avail.
I'm using the 30amp plug from my trailer to the generator and I've set my input limit to 30amps. Currently dynamic current limit is enabled, UPS function is off, power assist is disabled, ground relay is off, AC input controls are off, and the charger is off. It seems no matter what combination of these settings I attempt, I can't stay connected to the generator for more than a few seconds.
EDIT: It seems to work better when the generator is running on propane and not gasoline which is neat, but confusing and not ideal. Maybe that will give one of your geniuses a clue?