Mppt victron 250/100 +150/35

Dobrý deň, potrebujem pomoc, máme fotovoltaiku, victron multiplus invertor 48v 5000va panely 8x275 wp a mppt regulátor 150/35 victron +cerbo gxTeraz sme pridali panely 8x455 wpPripojené na dva reťazce po štyroch a mppt 250 mppt na 100 bol nastavený. pred zapnutím panelov pripojili panely a nič sa nedeje, nevyrába to žiadne napätie, ale na poistke je normálne napätie z panela, stačí ho pripojiť na mppt, tak sa stratí napätie, kde môže byť problem alebo co este treba nastavitOba mppt radice aj prvy aj druhy idu na tu istu zbernicuA zabudol som ze mam 3x pylontech us2000

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
ivan-botka avatar image
ivan-botka answered ·

Hello, I need help, we have photovoltaics, victron multiplus inverter 48v 5000va panels 8x275 wp and mppt regulator 150/35 victron +cerbo gx

Now we have added 8x455 wp panels

Connected to two strings of four and mppt 250 /100 mppt was set to 48 volts before switching on the panels, they connected the panels and nothing happens, it does not produce any voltage, but on the fuse there is normal voltage from the panel, just connect it to the mppt, so the voltage is lost, where could be the problem or what else needs to be set

Both mppt controllers and the first and second go to the same bus

And I forgot that I have 3x pylontech us2000

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mike Dorsett avatar image
Mike Dorsett answered ·

It seems like you may possibly have exceeded the maximum input voltage of the MPPT unit - though if the module Voc is <55V this should not be the case.

Please: carefully test the Voc at the module disconnect breaker, and also the Isc. The modules should be disconnected from the MPPT unit for this test.

Also, check that the connections to the MPPT unit are made correctly.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fanda avatar image
fanda answered ·

Dobrý den, Ivane!

Rád bych se Vás zeptal na Vaše dosavadní zkušenosti s provozováním 2 různých MPPT regulátorů (250/100 a 150/35) paralelně v jednom systému s Pylontech bateriemi a CERBO-GX. Zvláště mě pak zajímá, zdali CERBO-GX, potažmo Pylontech BMS správně řídí nabíjecí proudy obou regulátorů atd.

Proč se ptám: provozuji systém s 4,4 kWp panelovým polem, MPPT 250/70, CERBO-GX a 3 x Pylontech US3000C - dosud k mé maximální spokojenosti - a uvažuji o přidání 2 x 550 W panelů, které bych rád připojil přes MPPT 100/20 (parametry "sedí", větší MPPT nepotřebuji). Instalace k nalezení na VRM portálu pod "Past 2" ;-)


Předem moc děkuji!