controlling grid export : Quattro 48V/8000 or 48V/5000 or 48V/10000

Hello I have done several searches on the forum and looked through a good many topics by cannot find a simple answer to this question

I have also searched through the Quattro manual

so apologies if I missed it ..


Q) Is it possible to set the export level to the grid for the Quattro 48V/8000 ?


By default my DNO will accept 5kW to be exported to the grid, a little more than the usual 16A 230V 3.68kW. So I wondered if it's possible to set a specific level.


Thanks


MultiPlus Quattro Inverter ChargerESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
mvas avatar image
mvas answered ·

May be possible using ...

the Maximum Feed-In (watts) field

On the "Grid Feed-In" config screen

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@bladerunnervf

Yes you can in the ESS menu.

A caveat though, not all AC PV can be controlled so stick with DC PV on your install.