Connect AC to the programmable relay of Inverter RS

Hi!

In the manual of the Inverter RS you wrote: "Programmable relay which can be set for general alarm, DC under voltage or genset start/stop function, including minimum closed time and relay-off delay. DC rating: 4A up to 35VDC and 1A up to 70VDC"

Can I connect a 230V AC unit to this NO/NC/COM ports? It's a little relay, it consumes 0.4W

Thanks!

inverter rs
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
derrick thomas avatar image
derrick thomas answered ·

The manual lists the rating for the relay. If your proposed usage does not fall withing the parameters outlined in the manual do not connect it in that fashion. You can however use the relay to drive an external relay of your choice as long as the external relay driver is within the required specs.