VE Bus BMS with Smart Battery Protect

Hello,

We are having some trouble getting a Smart Battery Protect module to operate whilst connected to the VE Bus BMS load disconnect when using the non-inverting remote on/off cable. We can get it to work with a direct connection however; is the non-inverting remote on/off cable no longer required for this?

Lithium BatteryBMSBattery Protect
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stevo07 avatar image stevo07 commented ·

Bump......

0 Likes 0 ·
1 Answer
Martijn Coster (Victron Energy Staff) avatar image
Martijn Coster (Victron Energy Staff) answered ·

@Stevo07

No this cable is no longer needed. Why do you think it is?

best regards
Martijn Coster - Victron Energy