I have a system with a Multiplus 2 48V 5000VA which has a 48V 200Ah battery attached to it. Before I installed the ESS Assistant the battery would charge normally up to 55V. Now that I installed the ESS assistant it is not charging. Please help.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a system with a Multiplus 2 48V 5000VA which has a 48V 200Ah battery attached to it. Before I installed the ESS Assistant the battery would charge normally up to 55V. Now that I installed the ESS assistant it is not charging. Please help.
The image shows the inverter as off and no solar charger, that doesn't bode well for success, so presumably it hit the cutoff.
How are you running an ESS without solar?
The voltages also don't look right for lithium, so you would need to confirm what the manufacturer wants set, way too large gap for float to absorb for lithium.
Is this a managed battery - CAN attached?
If not how are you measuring SOC?
What ESS mode was configured? Did keep charged work?
Being an unsupported battery, there isn't a guide we can refer to, so the manufacturer should really help you with this.
Yes the system is tied with a grid tie Steca 4200 inverter and 4000W of solar panels. When the ESS was not installed the battery would charge normally but then if grid fails all sort of errors would pop up like low battery (when in fact the battery is full) The battery is exactly as a BYD 48V (exactly a copy of that) but I cannot find any system with in the Q&A with the Multiplus 2 48V with a 200Ah BYD settings. Any reference would help.