Inverter switch of when SOC is below 50 % in ESS mode and Grid failure

Hi

I use the ESS mode for my multi plus . But the Inverter switches of when SOC is below 50 % and the Grid in disconnected, even though minimum SOC is sett to 35 % How can I change this? screenshot-20230619-184100.png

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Robert Larsson

You will need to look at the programming on the inverter itself.

It will either be the dynamic cut off in ESS assistant or the shutdown on the inverter tab when using ve config.