I am connecting 4 AGM 12v batteries serial and parallel to get 24v. Is it OK to connect loads and shunt like in picture from opposite batteries or should I connect both battery terminals to collection post and from there to load and shunt?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I am connecting 4 AGM 12v batteries serial and parallel to get 24v. Is it OK to connect loads and shunt like in picture from opposite batteries or should I connect both battery terminals to collection post and from there to load and shunt?
@beavis your diagram gives an unbalanced current from each series battery pair.
1 series pair has 1 short link, the other series pair has 3 short links.
OK, so I will use same length cables on battery connections and connection post for loads.