Multiplus-II: Charger only and grid loss

Hello,

I would like to now what happens, when I switch a Multiplus II ESS via Modbus to Charger only / Inverter off and the grid fails? Does the ESS turn the Inverter on or have I to do that via GX by an automation?


Thanks

Edward

Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
derrick thomas avatar image
derrick thomas answered ·

ESS will not override the inverter switch setting. (Manual or virtual). If the switch is in "charger only" and grid is lost, the multi will not provide ac power.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

h3xf2x avatar image h3xf2x commented ·
Thanks for the clarification