question

dbollardini avatar image
dbollardini asked

Multiplus 2 parallel - Grid Charge current not lower than 7.5A

I'm using 2 x Multiplus II 3000/24 in parallel and all works fine. I use it on a big RV Car.
When i try to reduce grid current limit for old campgrounds the lowest limit is 7.5A / 230V.
( I remember it was a limit of 3.5 Ampere when standalone )

Is there a way to have a lower input current from grid ?
Only 1 Grid Input wire doesn't work. Multiplus goes to error when different inputs.

Many thanks for every idea

Dino

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
derrick thomas avatar image
derrick thomas answered ·

If you disable power assist you can set the input current limit lower. Only other option is to shut one of the multis off and reconfigure for stand alone.