We want to use 3xQuattro 10 kW for a 5 kW passenger elevator (lift).
Perhaps someone has experience with this type of load. How does the inverter respond to reverse power from the elevator to the inverter in battery mode?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Should be fine.
One of my customers has 3 Multiplus 15000VA and the biggest motor is around 12kW.
However, for this kind of load I suggest you to overdimmensionate the Batteries. Hence for 3x 10kVA at least 60kVA of batteries and the biggest cable you can get on.