SOLVED: Multiplus 2 48/5000 120v split phase, DC source output

Do I understand correctly that if I am running 2 Multiplus 2 48/5000 120v units in split phase configuration and they are connected to my DC battery bank that when in inverter mode I will be able to get a 120/240 split phase output?

Multiplus-IIdc systemsplit phase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Ed Jones avatar image
Ed Jones answered ·

Yes.

But in order to achieve the full 10kVA, you need to balance the loads across both inverters evenly. An Autotransformer can help remediate up to a 28A imbalance maximum, and not for long periods of time,