question

daschlichi avatar image
daschlichi asked

Cant change Settings for COS phi on QUATTRO 15K at Grid-Code VDE-AR-N 4105:2011-08

Dear Community,

- i have a 3-Phase Quattro 15K with ESS-Setup. (Firmware 497)
- Living in germany required me to setup a external NS-Protection by using Ziehl UFR1001E to comply with VDE-AR-N 4105:2011-08 or VDE-AR-N 4105: 2018-11

- As it is required by my local Network, i need to comply to some settings like for COSϕ, as it is described in DIN VDE V 0124-100 (VDE V 0124-100):2020-06.

- I know the QUATTRO 15K is certified to comply with ...
--> VDE-AR-N 4105: 2018-11...
...based on Test defined in ...
--> DIN VDE V 0124-100 (VDE V 0124-100): 2020-06. “Network integration of power generation systems – Low voltage"...
... by ...
--> Certificate-ESS-VDE-AR-N-4105-2018-11-Quattro-48-8000-110,-48-10000-140,-48-15000-200.pdf

Here comes the Problem:
- VE Configure 3 just offers me Grid-Code VDE-AR-N 4105:2011-08 and within this Grid-Code i also can´t make any changes, e.g. to COSϕ

windows-11.png

windows-11.pngcursor-und-windows-11.png

How can i either change settings on values like COSϕ (as it is for example possible in other Grid Code... (Here TOR Erzeuger Austria..)

windows-11.png

...or how can i get to select Grid-Code...

--> VDE-AR-N 4105: 2018-11 (with external NS-Protection) ... like i have seen it in Screenshots in in a different Post....
Screenshot with QUATTRO having VDE-AR-N 4105: 2018-11

.. where i assume i will automatically comply to the right settings defined by my local network provicer (like COSϕ .. settings)


MultiPlus Quattro Inverter Chargergridgrid parallel
windows-11.png (20.6 KiB)
windows-11.png (16.3 KiB)
windows-11.png (20.7 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@daschlichi

Is all your firmware on your inverters and software on your laptop up to date?


0 Likes 0 ·
daschlichi avatar image daschlichi Alexandra ♦ commented ·

Dear Alexandra,


Victron Connect 3 on Windows is up-to date, Inverters have "Firmware 497" (From November 2022) ..but actually i did not see something pointing towards this in the release-notes between then and today, also can`t imagene this was just added recently?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ daschlichi commented ·

Firmware 502 is available and in use. And likely there was a refinement. As it specifically mentions a change in German grid codes when using generators in 501.

screenshot-20230604-090735.jpg





0 Likes 0 ·
3 Answers
daschlichi avatar image
daschlichi answered ·

Dear Alex, will check this, might have overlooked this statement in the relase notes.

Thanks in advance, this looks very promising.
Will provide feedback asap.


Cheers, Daniel

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daschlichi avatar image
daschlichi answered ·

Dear Alex, i ran the Update und ingested the tunnel-file after the update into VE Configure.
Nothing changed, futrther Idea`s?
bildschirmfoto-2023-06-18-um-00-56-55-png.png


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daschlichi avatar image
daschlichi answered ·

Anyone else an Idea?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.