rigth config to Start/Stop a micro chp with Multigrid

Hi all,

my system consists of a multigrid 48/3000 with ccgx, smartmeter and a 12.8kWh battery storage from BYD, on the AC IN 1 a small PV is connected. It's all configured as ESS.

Further i have a on Grid micro chp on AC Out1 that should be switched off when the battery is full. So i config the K1 Relais to switch on 60% SOC and switch off 55,1V Batteryvoltage . The Problem is K1 do nothing ?!
Can it be the K1 only switches if no AC 1 is present in ? How can i solve the Problem ?
Or is the desired function only possible with the Relais of ccgx?


regards

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

try using the AUX1 or AUX 2 relay outputs as you can control when these close or open using the assistants.


If I am missing something here please attach a copy of you assistants setup

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alikante avatar image alikante commented ·

Hi Paul,

thanks for answering. I use the AUX1 ( K1 Relais ) with Assistant but the Switch do nothing, no Start if the Battery under 60% and no Stop if the Voltage is over 55V.

0 Likes 0 ·
1560666122733.png (21.0 KiB)
1560666172683.png (13.5 KiB)
1560666216816.png (7.3 KiB)
1560666246330.png (7.8 KiB)
1560666272147.png (6.6 KiB)
1560666312326.png (9.2 KiB)
1560666344297.png (7.3 KiB)
1560666407367.png (8.7 KiB)
Paul B avatar image
Paul B answered ·

I suspect you are missing the General Flag to ignore AC or AC in 1

I have attached what I do. keep in mind my Multi is a different model to yours.


1560676950582.png (25.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.