Can more than one Lynx BMS be connected to the same Cerbo GX? I understand only one would be used for the system view pages, but does it support multiple listed in the device list as it does BMVs or Smart Shunts?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Can more than one Lynx BMS be connected to the same Cerbo GX? I understand only one would be used for the system view pages, but does it support multiple listed in the device list as it does BMVs or Smart Shunts?
Hi, yes it does
Hi @banana,
You can select this manually or let the system select it automatically (default).
To do this, go to the DVCC menu and scroll down to the bottom of the menu where it says "Controlling BMS". At this menu item, press the spacebar to select the BMS to use for DVCC.
Note that this is a new feature that will only be released with version 3.00 and is not yet included in the last release version 2.94.
You can also find more information on beta testing in the beta test thread.
Hi Guys
im interested in this further as my client wants some more redundancy in a 2000AH system we are installing.
can we use 2 x lynx BMS to a Common Busbar and a single Cerbo with DC loads, Wake speed Regulators, and 2 x Quattro's
i dont think this can be done from what i can tell unless we Soley rely on the Contactor on each bank rather than DVCC and ATC and ATD
Thanks,