BMV 712 discharge floor / SOC

Hi, I have 4 x 270 Ah AGM batteries in parallel / series giving 24 volt and 540 ah monitored with a BMV 712

I have the discharge floor set to 50% as I don't want my batteries to fall below 50%

I want this set up so the relay will activate my generator when the batteries fall to 50% charge

For this to be correct do I need to set the SOC to 50% also or does the SOC calculate its 0% to 100% from the discharge floor setting of 50%?




BMV Battery Monitor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
pwfarnell avatar image
pwfarnell answered ·

The discharge floor is only used to calculate the time remaining figure. See

https://www.victronenergy.com/media/pg/SmartShunt/en/all-features-and-settings.html#UUID-a139a4fe-c67e-fb60-02f5-cb760de807fa

For SOC 0% = completely empty regardless of the discharge floor value. Therefore you need to set your generator relay to come on at 50%.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·

To add, afik it will alarm based on discharge floor