Setup: Cerbo GX + Multiplus II 48/5000 set up for ESS. No Solar.
What are the best settings to put the multiplus in an istandby/idle state? By standby I mean no ESS feed-in, no charging of the battery but allowing power to critical loads from the grid and act as a UPS should the grid fail.
The best I’ve managed to come up with is:
1. Cerbo GX relay connected to AUX1 of MP to disable ESS feed-in
2. Disable all scheduled charge
3. ESS mode set to Optimised
4. Multiplus set to ON
What does setting ESS mode to External do? Maybe it achieves the same thing?