question

anuck avatar image
anuck asked

Quattro AC2 out control for non-critical loads on grid down and low solar/batteryes?

Hi. Planning on installing 2x Quattro 10kVA for split 120/240 operation. At the beginning as a battery-only grid-tied backup.

Is it possible to control AC2 out for non-critical loads so that when the grid is down and batteries lower than X% it would shut down the AC2 out but with manual override?

The brochure says "[Auxiliary output 50a] Switches off when no external AC source available" - the forum mentions something about being able to program this using an assistant(?) - can I use something to override manually and add battery discharge % as an input?

Thanks!

MultiPlus Quattro Inverter Chargerquattro 10kva
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@anuck

Yes, with ve config and an mk3

Use the add assistant - relay - programmable relay. The use of ac2 out is listed as an option there.