Hello,
We have an RV with a Lithionics 48V RV-C lithium battery & BMS (fw v9.0.02), Cerbo GX (fw v2.94), Multiplus II 3kW (fw 492), SmartSolar 150/35 (fw v1.61).
Periodically the system experiences an error with these symptoms:
- The MPPT appears to lose communication with the battery
- It changes from Ext. Control to Float, and produces code #67
- The inverter AC output turns off
- The VE.Bus state changes from Inverting to Off
It seems to only occur during the times 7am - 9pm, never after 9p or before 7a. Perhaps it has to do with the solar cycle? In my mind this is not likely a wiring issue, since it doesn't occur overnight.
The issue has always been rectified automatically in a short period of time (1s to 1m, 41s).
See table below for instances of the error, and snips from VRM showing the other symptoms.
Any insight is welcome and appreciated. Thank you!
Device | Triggered by | Description | Started at | Cleared after |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/19/2023 13:27 |
19s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/18/2023 18:18 |
11s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/16/2023 9:50 |
1m, 3s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/15/2023 14:42 |
55s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/15/2023 13:52 |
1m, 5s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/14/2023 16:39 |
50s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/13/2023 18:07 |
1m, 6s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/9/2023 7:14 |
59s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/8/2023 12:15 |
56s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/6/2023 16:46 |
1m, 41s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/6/2023 15:32 |
59s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
4/4/2023 8:08 |
1s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
3/28/2023 13:23 |
3s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
3/27/2023 17:13 |
11s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
3/23/2023 12:20 |
47s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
3/1/2023 17:07 |
1m, 6s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/28/2023 16:16 |
1s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/26/2023 13:09 |
28s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/25/2023 16:12 |
23s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/20/2023 9:48 |
46s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/19/2023 15:41 |
27s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/18/2023 17:28 |
53s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/18/2023 16:39 |
22s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/17/2023 15:36 |
18s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/17/2023 14:23 |
17s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/16/2023 17:53 |
1m, 2s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/13/2023 19:09 |
58s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/13/2023 10:59 |
1m, 2s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/12/2023 13:42 |
55s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/7/2023 10:26 |
49s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/6/2023 10:22 |
53s |
Solar Charger - Solar PV array [279] |
Automatic monitoring |
Error code: #67 - No BMS |
2/5/2023 15:36 |
51s |