question

maciej-boike avatar image
maciej-boike asked

Victron with CFE battery compability.

Hello,
I would like to know if CFE 5100 battery from CF Energy company is compatible with Victron system?
https://www.cfenergygroup.com/

Description

General Data
• Battery Type: Lithium-Ion
• Battery Module: CFE-5100S
• Total Capacity: 5.1Kwh
• Nominal Charge / Discharge Power: 3.0Kw
• Operating Voltage: 48VDC to 56VDC
• Nominal Voltage: 51.2VDC
• Maximum Charging Voltage: 57.6VDC
• Nominal Current: 60A
• Recommended DOD: 90%
• Installation Type: Cabinet or Wall Mount
• Maximum Number of Parallel: 10 Units
• Series Connection: NO
• WIFI: Integrated WIFI Module (Use CFE APP)
• Colour: White

Regards

48v batterycfe
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Mike Dorsett avatar image
Mike Dorsett answered ·

see Victron Datasheet: Connecting other lithium systems to Multis and Quattros

This data sheet explains how do interface. From the voltage specifications, you should have compatibility, However do make sure that you have sufficient packs to handle the peak current of the inverter. 60A nominal current for a 100Ah pack is a bit light, but similar to pylontech and BYD packs at 0.5C.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image
Paul B answered ·

to know if its compatable, you would need to ask the battery manufacturer, otherwise if there are interface issue's you will have nowhere to go to get it sorted, the main area of concern would be the bms interface, make sure its compatible.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jamesstubberfield avatar image
jamesstubberfield answered ·

We are currently testing these batteries with Victron systems. We have found that the battery is recognised as a Pylontech module (quite common with 3rd party BMSs that are similar to Pylon). This is an issue since Pylon batteries are hard-coded in GX firmware to only be charged up 52.4V, to ensure system stability, so the CVL voltage that the CFE calls for (56.1V) is ignored by the Cerbo GX and therefore the battery cannot be charged above the 52.4V hard-coded voltage. I have read of other modules that suffer the same issue. We tried with Type A and Type B cables, and both times, the CFE module was recognised as a Pylontech, resulting in not being able to charge correctly.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jamesstubberfield avatar image jamesstubberfield commented ·
My own question in another post yielded a response that in the beta version v3 of VenusOS, this issue is now resolved. We will test our CFE with a beta version of firmware, and report back here for your reference.
0 Likes 0 ·
xzv avatar image xzv jamesstubberfield commented ·

Did you succeed in getting that 51.2 V system to work correctly?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ xzv commented ·

The problem was with the BMS announcing as pylontec which are usually 15s batteries but are managing the 16s batteries.

The issue was the GX would not let the 16s battery charge fully since for anoylotec this is it correct.

There was a fix for this in GX V3 00.

0 Likes 0 ·
kajwek avatar image
kajwek answered ·

It seems that CFE has completed compatiblity with Victron Cerbo GX, here is the document:

CFE Inverter Communication Setting 0612 - updated version.pdf


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources