I've been noticing a high grid usage since version 500 of the MP2 fw.
My system is setup in a ESS zero feed configuration and with a setpoint of 0. The normal grid consumption interval is between 70 and 180w. The house consumption is not that high, normally at 450w, so the grid power usually is a 1/3 of the total consumption.
Also with this problem above, I also noticed that the system always overcharges the battery. I have 14s/13kWh of lithium configured at a max. voltage of 56.8, but it continuously gets charged to 57.4v. I guess that the only thing that prevents it from overcharging it's the BMS that kicks in at 4.09S for balancing.
Configuring DVCC to 56v has no effects. DVCC seems totally inutilized. Current limiting also doesn't work.
Is there any way of opening an issue for this kind of bugs so we can trace them and know if they are being followed or addressed by Victron technicians?
Is there a way of rolling back the MP2 fw to a well-known version?
My system: MP2-5K / 14s-13kWh-57v Lithium / BMS not integrated / Smartshunt / MPPT 150/80 ve.bus connected / Fronius 5K integrated.
EDIT:
When the Max.Charge voltage is set to 56, the battery gets charged up to 56.7. That seems in line with the numbers I got when I had the voltage set to 56.8.
Also I've noticed that when the charge is completed, the grid setpoint offset seems to normalize.
So it seems to me that may be a problem with the ESS charge algorithm mapping. There was plenty sun available during the charge, the system was throttling the Inverter and Charger, but at the same time getting energy from the grid to charge the batteries.
EDIT:
That's insane... no one?