question

rona avatar image
rona asked

lynx bms 500 hot when loaded.

Hi new installation and while testing the bms is reaching 81.4 deg celcius when a 200-300 amp load is applied to the system.

The cooling fans are not turning on.

When i charge the batteries with a similar charge rate then the fan does turn on and cools the bms,

any thoughts??

lynx bms
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
kevgermany avatar image
kevgermany answered ·

Contact the dealer. Sounds like it needs testing/replacing.

But you say fans come on. Which fans?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rona avatar image
rona answered ·

the two fans inside the lynx bms next to the contactor turn on but only when charging batteries.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
Best check with the dealer. Something's not right and there's nothing we can do online, sorry.