Quattro inverter overloas but Phoenix doesn't

I've replaced Phoenix with Quattro. Both have identical inverters according to datasheets. 24v 5000VA 230v.

Phoenix was rarely overloaded, Quattro constantly. Even a coffee maker can trigger it.

Phoenix never showed "Temperature" warning while working in 45C°. Quattro works in 35C°, shows a warning and then shuts down with an error.

Typical scenario: 10A load for 2 hours triggers a temperature warning first, then an error and Quattro shuts down. Ambient temperature is 35C°. Fan sounds like it's working.


What could be the reason? Broken Quattro?



MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
shmol avatar image
shmol answered ·

Looks like I've fixed it.

The problem was in connectors from transformers. There's two transformers. One of them was completely disconnected. Another one was just loose. So I fixed the connectors with pliers and now everything looks fine.

At least it's able to start a 1.5kw motor (so 9kw at start).
I believe that is is a quality control issue. There was a problem from the start a recent shipping by UPS make it more appearant.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

Loose connection somewhere?

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shmol avatar image shmol commented ·
But how this can exaplain the temperature error? It even happened with no AC load (load switched to genset).
0 Likes 0 ·
snoobler avatar image snoobler shmol commented ·
Loose connections at AC in or out would generate substantially more heat.