Where can i find the Low Battery voltage setting?

I've got a system with 400ah of 48v LiFePo4 batteries and I'm constantly getting low battery Voltage warnings. But they seem to be set at 52.08 volts which seems a bit high.

I have an ESS running in Battery life mode. Images of setting below:

I can't for the life of me find the setting that is causing this alarm. Can anyone point me in the right direction?

Can I also get a sanity check on my settings? Including recommended settings for the DC Input Low Voltage Shutdown?


1679731781737.png1679732023223.png

1679732107398.png

1679732183877.png

1679732202361.png

Lithium Battery48v batterylow battery warning
1679731781737.png (107.4 KiB)
1679732107398.png (246.7 KiB)
1679732183877.png (117.2 KiB)
1679732202361.png (67.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html#UUID-7435bdda-8f3f-81c2-a1a6-dc8f1c9b2f8f

Your dynamic cut-off values are to high.
I would recommend to set all to 48V or 47V.

You also have to check the Inverter Tab.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

de1nonly avatar image
de1nonly answered ·

Thank you, that was it!!! I had more reasonable values set in the Inverter tab but apparently it is overwritten when an ESS is running with the dynamic cut-off values.