Multiplus 12/3000 error #24

We have dual Multiplus 12/3000 units wired in split phase to a Victron Autotransformer. The system is now faulting with error #24 when connected to shore power. This has been traced to the slave inverter. The back feed relay seems to be stuck closed. I would appreciate any available feedback. Thank you.


I have performed all the testing steps laid out in the error codes document: https://www.victronenergy.com/live/ve.bus:ve.bus_error_codes">https://www.victronenergy.com/live/ve.bus:ve.bus_error_codes

This occurs with no load on the inverters. Main breaker off.

We are connected to a 50 amp shore power plug working properly with other systems.


Step 1 video of error led's:

Step 2 disconnect input and output wiring:

img-1534-small.jpeg

Step 3 measure resistance:

Input and output neutrals - 95 ohms

Input and output line - 0 ohms


After reading all the other cases for error 24 on this community I have also done the following:

Removed inverter from split phase system, configured for stand alone.

Disconnected all AC wiring, power unit on - no issue

Disconnected AC input wiring only - no issue

Disconnected AC output wiring only - error 24 immediately present when shore power applied.

MultiPlus Quattro Inverter Charger
img-1534-small.jpeg (33.7 KiB)
img-1533.mp4 (7.2 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
usernamepasswordbs avatar image
usernamepasswordbs answered ·

Did you ever get any solution to this problem ?

I have error 24 occurring when grid power is restored after a power cut so similar to your connecting of shore power.