MPPT Over paneling

Hi,


Please can you advise, I want to know if i can add more panels to my setup below ?


Setup :


3 * 24V/3000 Multiplus 1

3 * 250/100 MPPT


I have 5 panels on each controller, with a total voltage of 228V, which means i have 22V capacity remaining. Over the past 90 days "summer" i never went over 194V per controller. Can i add more panels to take me to 250V? What will happen if my Voltage exceeds 250V? Victron recommends over paneling by 30% does this also refer to the PV Voltage ?

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Denzel

No. The 250v string is a hard limit. 194v is the panel under load and that is not the voltage used for sizing.

You can add a second string to the charge controller (of exactly the same config).

Then your set up will be over sized without breaking the input current limit or the VOC limit.