question

pchristou avatar image
pchristou asked

Multiplus Monitoring

Dear Sir or Madam,

I have installed a Multiplus C12/2000/80-30, a Smart Solar MPPT and a BMV-700.

I also have in my system a PLC and customized monitoring.

Can I receive all the data from these devices through the PLC?

Or should I purchace a Color Control device?

If I must take the Color Control, can I connect it to my PLC?

monitoring
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

The MultiPlus communicates using the proprietary VE.Bus protocol. It would be best to use a Venus device like CCGX or the more cost effective Venus GX which doesn't have a display.
Then you can enable the ModbusTCP service on the Venus device and communicate with a PLC that way.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pchristou avatar image pchristou commented ·

Can I use the color control device and also the plc in parallel?

Thank you very much!

0 Likes 0 ·